下面是Glover原文內容 被李元拿掉不少 It becomes diffcult and in some cases impossible to coordinate overcurrent relays when there are two or more sources at different locations. Consider the system with two sources shown in Figure 10.22. Suppose there is a fault at P1. We want B23 and B32 to clear the fault so that service to the three loads continues without interruption. Using time-delay overcurrent relays, we could set B23 faster than B21. Now consider a fault at P2 instead. Breaker B23 will open faster than B21, and load L2 will be disconnected. When a fault can be fed from both the left and right, overcurrent relays cannot be coordinated. However, directional relays can be used to overcome this problem. 目前電力系統還沒看得很熟 你就先自己看看分析八 -- ※ 發信站: 批踢踢實業坊(ptt.cc), 來自: 1.165.185.67 ※ 文章網址: http://www.ptt.cc/bbs/Examination/M.1410430881.A.C5E.html
crazymax: 上面說法 是說啟斷B23速度是快於B21 造成P2發生錯誤時 09/11 18:30
crazymax: B23會先打開 09/11 18:31